Exit Signs in Dormitories?

elecshop

Member
Location
FL, USA
Occupation
Electrical Engineer
According to FBC, means of egress is not required in dwelling units and sleeping units in groups R-1, R-2, and R-3. But what about the corridor that serves individual sleeping units (6 of these) in a mixed occupancy type of building (occupancy U & R-2) ?

Also, 1013.1 exceptions from FBC says that exit signs exit signs are not required in occupancy U and dwelling units in R-2. Does this include the egress paths? Not that I have 3 different exits in this building. The other exception (2) which says main exterior exit doors that are obviously identifiable as exits to not need exit signs if approved by building official.

Any thoughts?
 

ron

Senior Member
The code section you are referencing is pasted below for other to review.

It provides for exceptions, but does not provide for relief from other means of egress in the building, such as egress corridors serving the individual sleeping units.

1725648294908.png
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
According to FBC, means of egress is not required in dwelling units and sleeping units in groups R-1, R-2, and R-3. But what about the corridor that serves individual sleeping units (6 of these) in a mixed occupancy type of building (occupancy U & R-2) ?

Also, 1013.1 exceptions from FBC says that exit signs exit signs are not required in occupancy U and dwelling units in R-2. Does this include the egress paths? Not that I have 3 different exits in this building. The other exception (2) which says main exterior exit doors that are obviously identifiable as exits to not need exit signs if approved by building official.

Any thoughts?
As soon as you step out of your unit into a common hallway, you need exit signs.
 