Have exits feed from normal panel in hospital. There is no ATS feeding panel. Find it a little odd an maybe even against code that they are fed from normal panel. Think it's considered life safety.
+1Are they battery backup?
No they aren't. If they are battery back up fixtures they have to be fed from the normal branch, they have to be fed from the local lighting circuit.Yes, arent all?
Which may or may not be on an emergency panel, local circuit must fail before battery takes over.No they aren't. If they are battery back up fixtures they have to be fed from the normal branch, they have to be fed from the local lighting circuit.
Roger
they have to be fed from the local lighting circuit.
Some are some aren't.Exit signs are not unit equipment.
Whether or not they are required to be illuminated when normal power is lost also would come into this.So.. what's the local lighting ckt origin? I would think that's the answer. Whether against code would be a definition of the space.
Sent from my SM-G930V using Tapatalk
Whether or not they are required to be illuminated when normal power is lost also would come into this.
I think it is pretty common to put them on with local lighting, but these are not necessarily the same thing as emergency lighting either. Sometimes exit signs aren't even required to be illuminated, just a placard is acceptable, lighted signs often get installed anyway.
Op never mentioned whether this is a hospital, if not the mentioned 517 article doesn't apply though OP did mention life safety, which may or may not mean a hospital is involved.
Oops' not even that long of an OP, and I read right over it when trying to decide to make that reply:slaphead:The OP did state it was a hospital.
Sure they are, look at "Exits" in the index and notice it takes you to 700.12(F), 700.16, as well as 517 sections.Exit signs are not unit equipment.
Have exits feed from normal panel in hospital. There is no ATS feeding panel. Find it a little odd an maybe even against code that they are fed from normal panel. Think it's considered life safety.