No.Can expanding foam cut through a wire when sprayed into a raceway?
Using open cell foam as a duct seal? :lol:Should expanding foam be inside a raceway?
With out a doubt, yes. If I or some other put it there I would expect nothing other.Should expanding foam be inside a raceway?
Just don't try that in an open bottom, ladder type cable tray though.With out a doubt, yes. If I or some other put it there I would expect nothing other.
Well for NM cable 334.80 would apply.
Where more than two NM cables containing two ormore current-carrying conductors are installed, withoutmaintaining spacing between the cables, through the sameopening in wood framing that is to be sealed with thermalinsulation, caulk, or sealing foam, the allowable ampacityof each conductor shall be adjusted in accordance withTable 310.15(B)(3)(a) and the provisions of 310.15(A)(2),Exception, shall not apply.