Hi I am new to site .
Retired Highvoltage Electrcian .Not a lot of residential experience but 35 years high voltage.
Doing meter stand for Generator 200ft away from home.
Stand has stub poles 2.5 inch PVC Conduit going into DB2 conduit just secured @ 1 end allowed to move freely in DB2 12inches of movement
Other Stub for generator and Transfer switch secured @ 1 end other end. Above floor trench in ground (12 inches) allowed to move freely .
I am assuming no PVC Expansion bellows is needed
Due to not being secured on both ends .
2nd question is that Bell bushings hard to come by on backorder from suppliers ,
can I get away with terminal bushing with 2 locknuts and plastic bushing on end
where cable from trench enters conduit .
Other option is a 90 sweep in trench with bell end and coupling . But now I have straight PVC to 90 sweep 24 inch radius in horizontal partly in trench
now do I need Expansion bellows .
Is it safe to say that Even with large temp differential and conduit is under 25 ft as long as its not fixed on both ends .
expansion bellows is not needed .
Any of your input be much Appreciated .
Thanks Viper
Retired Highvoltage Electrcian .Not a lot of residential experience but 35 years high voltage.
Doing meter stand for Generator 200ft away from home.
Stand has stub poles 2.5 inch PVC Conduit going into DB2 conduit just secured @ 1 end allowed to move freely in DB2 12inches of movement
Other Stub for generator and Transfer switch secured @ 1 end other end. Above floor trench in ground (12 inches) allowed to move freely .
I am assuming no PVC Expansion bellows is needed
Due to not being secured on both ends .
2nd question is that Bell bushings hard to come by on backorder from suppliers ,
can I get away with terminal bushing with 2 locknuts and plastic bushing on end
where cable from trench enters conduit .
Other option is a 90 sweep in trench with bell end and coupling . But now I have straight PVC to 90 sweep 24 inch radius in horizontal partly in trench
now do I need Expansion bellows .
Is it safe to say that Even with large temp differential and conduit is under 25 ft as long as its not fixed on both ends .
expansion bellows is not needed .
Any of your input be much Appreciated .