Expansion couplingon pvc service riser

Status
Not open for further replies.

jaykilty

Member
Location
mass
Will be doing a service riser in PVC. It will have a couple of bends in it. I was picked up once for not installing a expansion joint because the riser had bends. The inspector showed me the article but of course I can’t remember it now can anyone help me out here?
 
It’s 2 fixed points that require the expansion fitting, if your conduit runs straight up, even with a saddle in the middle, to the weatherhead no expansion is required.
If you hit a bend that changes direction of the pipe run you have to have one.
 
For PVC its 352.44.

352.44 Expansion Fittings. Expansion fittings for PVC
conduit shall be provided to compensate for thermal expansion and contraction where the length change, in accordance
with Table 352.44, is expected to be 6 mm ( 1 ⁄ 4 in.) or greater in a straight run between securely mounted items such as boxes,
cabinets, elbows, or other conduit terminations.
 
It’s 2 fixed points that require the expansion fitting, if your conduit runs straight up, even with a saddle in the middle, to the weatherhead no expansion is required.
If you hit a bend that changes direction of the pipe run you have to have one.
Yup I will have a change in direction. Any idea of the article? I don’t see that in 352.44
 
Depending on the location of the supports on each side of a 90° bend and the amount of calculated expansion or contraction, the 90 can be used as the expansion device.
 
But if the adjacent side of the 90 is supported closely, the 90 itself has to be considered as a fixed point at the end of a straight run.

Sent from my XT1585 using Tapatalk
 
But if the adjacent side of the 90 is supported closely, the 90 itself has to be considered as a fixed point at the end of a straight run.

Sent from my XT1585 using Tapatalk
How can that be considered a fixed point when using expansion clips which are required as far as I know
 
It's worth mentioning, that if your install dictates an expansion fitting, it goes without saying you need straps/supports capable of allowing the conduit to slip.

Using regular strut straps or similar is a no go.
 
How can that be considered a fixed point when using expansion clips which are required as far as I know
If you have a horizontal run that is subject to thermal expansion/contraction of more than 1/4 inch, an elbow or conduit body that makes a vertical deflection can be allowed to move and no additional expansion fitting is necessary, but if after making that vertical deflection the next support on the vertical portion is so close to the elbow/conduit body that it effectively secures the elbow or conduit body from horizontal movement - then you still need additional expansion fitting on the horizontal portion of the run - hope that makes sense.
 
How can that be considered a fixed point when using expansion clips which are required as far as I know
Expansion clips allow motion parallel to the conduit run, not perpendicular to it. When I said "adjacent side" I was referring to the side of the 90 perpendicular to the run in question.