Expansion Fitting- Asphalt

Always4

Member
Location
Philadelphia
Occupation
Electrician
Is it typical to install PVC expansion fitting on conduits protruding vertically from asphalt? The inspector claims they are needed for thermal expansion. I can’t find anything in the NEC specifically relating to asphalt. We are currently still on 2017 code cycle.

Background-
-Perviously installed- 2” PVC underground Service conduit has an expansion fitting

-Installing- 1- 1 1/2” and 1- 3/4” conduit
-Terminates in a PVC junction box 8” above grade. It will likely require relocating box as there isn’t much space for an expansion fitting.
 
Expansion fittings are typcially used for two reasons, 1) expansion/contraction of PVC conduit and 2) earth movement.

At only 8" of raceway 1) would not apply.

Regarding 2) will the conduit be able to move after installation? {300.5(J)}
 