T T-minator Member Location chicago, IL Dec 6, 2013 #1 Is it code to use a box to seal tight to box connection instead of an expansion fitting?
Smart $ Esteemed Member Location Ohio Dec 6, 2013 #2 T-minator said: Is it code to use a box to seal tight to box connection instead of an expansion fitting? Click to expand... There's nothing in the Code which prohibits it.
T-minator said: Is it code to use a box to seal tight to box connection instead of an expansion fitting? Click to expand... There's nothing in the Code which prohibits it.
N Nom Deplume Senior Member Location USA Dec 6, 2013 #3 I would use flex instead, unless it is in a wet location.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Dec 7, 2013 #4 What is the application? If in a dry location then it would need to comply with the flexibility requirement. 350.10(1) Where conditions of installation, operation, or mainte- nance require flexibility or protection from liquids, va- pors, or solids Click to expand...
What is the application? If in a dry location then it would need to comply with the flexibility requirement. 350.10(1) Where conditions of installation, operation, or mainte- nance require flexibility or protection from liquids, va- pors, or solids Click to expand...