expansion joints

Status
Not open for further replies.
Re: expansion joints

You have to answer that question yourself depending on the area in which you are located and the temperature range you expect. See section 352.44 for the instructions. :D
 
Re: expansion joints

However, if frost lifts the slab on which the mobile home is mounted you will have a few problems besides a broken conduit.

You do not want to bury an expansion joint in the ground. In at least 1 mobile home park around Akron, Ohio tree and grass roots have penetrated O-ring gasketed joints in PVC sanitary sewer pipe. A PVC or steel conduit expansion joint also has similar O-rings.

What I would do is to put a sleeve around the feeder conduit where it emerges from the slab so that there is no solid connection. I would then run liquidtight nonmetallic conduit from the rigid PVC stub to the conduit that goes from the underside of the mobile home to the pnaelboard. I would also use a PVC pull box between the rigid PVC and flexible PVC conduits. Flexible PVC conduit has a very high coefficient of friction.
 