Joe Corbin
Member
- Location
- Key West Florida
- Occupation
- Master Electrician
Does anyone have experience pulling aluminum pvc coated MC thru sch 40 pvc conduit. We are to install this cable in /thru pvc sch 40 conduit from the vfds to the motors. The conduit fill ratio is good. However the maximum bend radius for two sizes of the cables is very tight. On 4" conduit the standard radius of a 90 is 16". The 500mcm cable to be installed has a OD of 2.290 x 7 = 16.03" maximum radius bend. For the 3" conduit the standard radius of a 90 is 13". The 250mcm cable OD is 1.845 x 7 = 12.915 maximum radius bend. The ODs listed are for just the metalic sheath only, with the pvc jacket coating the OD is slightly larger for both cables. The pvc conduit is already installed. I am wondering how hard this will pull or if the 90s/fittings should be changed out to larger special radius 90s. Has anyone had experience with this type of installation? I may have to just try one pull to find out.