161108-1448 EDT
Following are three results of a simple experiment switching an inductance. The purpose of this experiment was to observe the arc voltage drop following the opening of a mechanical switch at atmospheric pressure in air. This was a quick experiment consisting of a DC source in current limiting to set the initial current in inductor, a reverse biased diode across current source, an ordinary Ohimite power resistor, 1 ohm, for current measurement (means it was very slightly inductive), 1 ufd capacitor in parallel with said 1 ohms resistor, a single Potter and Brumfield KUP relay contact as the switch (10 A rating), and the transformer primary wired in parallel of a A41-175-16 Standard Transformer transformer.
Initially upon opening of the switch contact the switch voltage drop appears to be a constant of about 15 to 20 V. As current drops the voltage gradually increases to around 50 V.
If the arc extinguishes before near zero current, then a rather large voltage spike appears. The stored magnetic energy has to go somewhere.
A more controlled experiment is needed with higher initial current, and I believe we will see the initial voltage drop stay around 15 V.
Many trials were required to get the following three plots.
Blue is switch voltage, and red is current.
.
.
.
.
.
Following are three results of a simple experiment switching an inductance. The purpose of this experiment was to observe the arc voltage drop following the opening of a mechanical switch at atmospheric pressure in air. This was a quick experiment consisting of a DC source in current limiting to set the initial current in inductor, a reverse biased diode across current source, an ordinary Ohimite power resistor, 1 ohm, for current measurement (means it was very slightly inductive), 1 ufd capacitor in parallel with said 1 ohms resistor, a single Potter and Brumfield KUP relay contact as the switch (10 A rating), and the transformer primary wired in parallel of a A41-175-16 Standard Transformer transformer.
Initially upon opening of the switch contact the switch voltage drop appears to be a constant of about 15 to 20 V. As current drops the voltage gradually increases to around 50 V.
If the arc extinguishes before near zero current, then a rather large voltage spike appears. The stored magnetic energy has to go somewhere.
A more controlled experiment is needed with higher initial current, and I believe we will see the initial voltage drop stay around 15 V.
Many trials were required to get the following three plots.
Blue is switch voltage, and red is current.
.
.
.
.
.