Twoskinsoneman
- West Virginia, USA NEC: 2020
- Facility Senior Electrician
I was talking to a tech the other day and he told me when he was doing a PM to check the cells of each battery in a UPS string he got shocked when his arm was in contact with one of the battery terminals and the rack that hold the batteries. Out of curiosity I took some reading and was hoping one of you geniuses could tell me what I'm seeing. It is an Eaton 9315 500kVa 480v UPS. It has a string of batteries, 2.75 volts per cell 240 cells. I figured if the string were grounded on the negative side you could get shocked between the rack and any number of the battery terminals once the potential was high enough. What I found has me baffled a little though.
From the positive wire to the negative 540vdc, 0vac
From either positive or negative to ground ~270vdc, 167vac
From the "middle" cell to ground 0vdc, 167vac (this is real voltage measured with a low-impedance path)
From various cells there is an accumulative dc voltage to ground, further from the middle cell the higher the potential to ground.
From every cell there is 167vac to ground.
There is no connection from the battery string to ground unless it's in the UPS which I did not open up. I guess since there is 0vdc from the "middle" cell to ground I was looking for some connection to ground at that cell but there is none.
Where might the indicated 167vac be coming from?
Why would the middle of the battery string be indicating 0.0vdc?
Thanks
Oh, here is a crappy paint drawing to help a little. Obviously there are more cells than shown.
Thanks