After looking more into Chapter 500 (using the 2008 NEC), I am now more confused than ever
Some follows ups and general questions related to a
Class I Division II location:
I couldn’t find a definition of arc-producing equipment but it looks like all equipment in the informational note in 500.8(B)(1) are potential sources of ignition
(Luminaires and other heat-producing apparatus, Switches, Circuit breakers, Plugs and Receptacles). 500.8(B)(1) indicates that this equipment is to be identified for use in the specific hazardous location.
For reference, 500.8(B)(1) Approval for Class and Properties:
Equipment shall be identified not only for the class of location but also for the explosive, combustible, or ignitible properties of the specific gas, vapor, dust, or fibers/flyings that will be present. In addition, Class I equipment shall not have any exposed surface that operates at a temperature in excess of the ignition temperature of the specific gas or vapor. Class II equipment shall not have an external temperature higher than that specified in 500.8(D)(2). Class III equipment shall not exceed the maximum surface temperatures specified in 503.5.
Question: Just verifying that all luminaires, switches, circuit breakers, plugs and receptacles potential sources of ignition? Also, any ideas why motors aren’t mentioned?
Question: I don’t see HVAC equipment mentioned. If the equipment is outside of a hazardous area but has ductwork inside a hazardous area (which draws air back into the equipment), could there be a potential for an explosion at the equipment?
Going onto 500.8(C) Marking, it indicates:
Equipment shall be marked to show the environment for which it has been evaluated. Unless otherwise specified or allowed in (C)(6), the marking shall include the information specified in (C)(1) through (C)(5):
(1) Class. The marking shall specify the class(es) for which the equipment is suitable.
(2) Division. The marking shall specify the division if the equipment is suitable for Division 2 only. Equipment suitable for Division 1 shall be permitted to omit the division marking.
(3) Material Classification Group. The marking shall specify the applicable material classification group(s) in accordance with 500.6.
(4) Equipment Temperature. The marking shall specify the temperature class or operating temperature at a 40°C ambient temperature, or at the higher ambient temperature if the equipment is rated and marked for an ambient temperature of greater than 40°C. The temperature class, if provided, shall be indicated using the temperature class (T Codes) shown in Table 500.8(C). Equipment for Class I and Class II shall be marked with the maximum safe operating temperature, as determined by simultaneous exposure to the combinations of Class I and Class II conditions.
(5) Ambient Temperature Range. For equipment rated for a temperature range other than –25°C to +40°C, the marking shall specify the special range of ambient temperatures in degrees Celsius. The marking shall include either the symbol “Ta” or “Tamb.”
And in 500.8(C)(6) Special Allowances it indicates:
(a) General-Purpose Equipment. Fixed general-purpose equipment in Class I locations,
other than fixed luminaires, that is acceptable for use in Class I, Division 2 locations shall not be required to be marked with the class, division, group, temperature class, or ambient temperature range.
Question: I can’t find a definition of “General-Purpose Equipment”. What is this referring to in 500.8(C)(6)?
Question: It looks like Luminaires in a Class I Division II area is required to be marked with the Class, Division, Group, Equipment Temperature, and Ambient Temperature range – is that correct?
Question: It looks like in a Class I Division I area, all luminaires, switches, circuit breakers, plugs and receptacles are required to be marked with the Class, Division, Group, Equipment Temperature, and Ambient Temperature range – correct?
In Looking at 500.7 Protection Techniques:
(A) Explosionproof Apparatus. This protection technique shall be permitted for equipment in Class I, Division 1 or 2 locations.
(B) Dust Ignitionproof. This protection technique shall be permitted for equipment in Class II, Division 1 or 2 locations.
(C) Dusttight. This protection technique shall be permitted for equipment in Class II, Division 2 or Class III, Division 1 or 2 locations.
(D) Purged and Pressurized. This protection technique shall be permitted for equipment in any hazardous (classified) location for which it is identified.
(E) Intrinsic Safety. This protection technique shall be permitted for equipment in Class I, Division 1 or 2; or Class II, Division 1 or 2; or Class III, Division 1 or 2 locations.
(F) Nonincendive Circuit. This protection technique shall be permitted for equipment in Class I, Division 2; Class II, Division 2; or Class III, Division 1 or 2 locations.
(G) Nonincendive Equipment. This protection technique shall be permitted for equipment in Class I, Division 2; Class II, Division 2; or Class III, Division 1 or 2 locations.
(H) Nonincendive Component. This protection technique shall be permitted for equipment in Class I, Division 2; Class II, Division 2; or Class III, Division 1 or 2 locations.
(I) Oil Immersion. This protection technique shall be permitted for current-interrupting contacts in Class I, Division 2 locations as described in 501.115(B)(1)(2).
(J) Hermetically Sealed. This protection technique shall be permitted for equipment in Class I, Division 2; Class II, Division 2; or Class III, Division 1 or 2 locations.
(K) Combustible Gas Detection System. A combustible gas detection system shall be permitted as a means of protection in industrial establishments with restricted public access and where the conditions of maintenance
Question: It looks like that lighting fixtures in a Class I Division II area are required to either be explosion proof or hermetically sealed for all practical purposes. I don’t think the other protection techniques are practical or apply. Thoughts?