georgeswe
Senior Member
- Location
- The Republic of Southern California
We are doing a project where the electrical engineer is installing explosion proof lighting in a car dealership new/used oil storage room. This raised a red flag as to the fact that we have never installed this type of fixture in these spaces before. I know that motor oil is a Class II liquid (flash-point is higher than 100 deg F) Typically a garage area is Class 1 Div II and we do not enter anywhere in the 18" off the floor. I looked at the code section 514.3(B)(1) under lubrication or service room - without dispensing. And it looks like the classification is the same Class I Div II, and by this, we would not need to install this type of fixture in the space as long as it it installed above 18". If anyone could help me out in finding out if we do need this type of lighting in this space. Or any code reference numbers so I can help challenge the use of a VERY expensive fixture where it is not needed.