I I have a class 2 group g motor and I am being told to replace it with a class 1 group d motor, is this a safe or allowable action?
Grain dust is the hazard.What conditions are there to create a hazardous location is the first thing that is needed to be known.
The key application is Section 502.5. The next consideration is the Division and Section 502.125 (A) or (B) as applicable. If it is Division 2, in most cases, it isn’t even necessary to be specifically identified for Class II.I I have a class 2 group g motor and I am being told to replace it with a class 1 group d motor, is this a safe or allowable action?