For conduit or tubing nipples less that 24" in length, does the 60% fill rule apply for Class 1, Division 1 and 2 explosion proof seal fittings that normally require a 25% fill?
This question is based upon infromation obtained from NEC Chapter 9 Tables (4) Where conduit or tubing nipples having a maximum length not to exceed 600 mm (24 in.) are installed between boxes, cabinets, and similar enclosures, the nipples shall be permitted to be filled to 60 percent of their total cross-sectional area, and 310.15(B)(2)(a) adjustment factors need not apply to this condition.
Dale Hayes
	
		
			
		
		
	
				
			This question is based upon infromation obtained from NEC Chapter 9 Tables (4) Where conduit or tubing nipples having a maximum length not to exceed 600 mm (24 in.) are installed between boxes, cabinets, and similar enclosures, the nipples shall be permitted to be filled to 60 percent of their total cross-sectional area, and 310.15(B)(2)(a) adjustment factors need not apply to this condition.