I'm writing a company wide specification / procedure on building control cabinets, and I want to put a limit / rule for exposed copper on power wires traveling from the main breaker all the way to the terminal blocks (with components in between). Does NEC call out a maximum exposed copper when making these connections? Is any allowed or should the clamp (on a contactor for example) make contact with the insulation? Any help would be appreciated, as I've searched through the NEC without luck (doesn't mean its not there, just maybe looking in the wrong section)
Control cabinets for industrial machinery would fall under NFPA79.
Section 12.2.1.3 would apply to general circuits:
12.2.1.3 Exposed, nonarcing, bare, live parts operating at
50 volts ac (rms value) or 60 volts dc or more within an enclosure
or compartment shall have an air space of not less than
13 mm (1⁄2 in.) between them and the uninsulated walls of the
enclosure or compartment, including conduit fittings. The air
space for uninsulated doors of the enclosure shall be not less
than 25 mm (1 in.). Where barriers between metal enclosures
or compartments and arcing parts are required, they shall be
of flame-retardant, noncarbonizing insulating materials. ...
This is what (conceptually) Jumper was referring to.
But technically, the code(s) don't absolutely require that your conductors be insulated at all, think bus bars. It's just that if not insulated, they are mounted in a manner that is safe. Insulation makes that a whole lot easier though. :roll:
Then still:
3.3.41 Exposed (as applied to live parts). Capable of being
inadvertently touched or approached nearer than a safe distance
by a person. It is applied to parts not suitably guarded,
isolated, or insulated. [70:100]
The end of that is a reference indicating it is the definition used in NFPA70 (the "NEC") section 100 as well.
"Suitably" is one of those nebulous terms that gets people in trouble. If someone gets hurt, your idea a "suitably" can be shown, by a good lawyer, as being incorrect, evidenced by the injury in question. So in that context, the answer would be zero exposed cable, right? It's not practical of course, but it's also not spelled out as an absolute distance either. I'd say use common sense. But since you are tasked with writing a spec, I think it's going to come down to you picking a number and being willing to stand by it. 1/8" sounds like a workable value to me, others might say 1/4". the use of "finger safe" IEC components would be something to think about too. Although not in any NFPA documents, that concept, IEC-60529, says that "finger-safe" as defined by IP-2X, is if a 12.5 mm (1/2 inch) metal sphere probe 80 mm in length (the size of an average little finger) is unable to make contact with any potentially energized circuit component within the assembly. I've seen that standard used.