Exposed Electrical Work

Status
Not open for further replies.

RedSafety

New User
Location
San Jose
Occupation
Safety Coordinator
Replacing a breaker in a 480v 3phase panel that is part of a distribution cabinet. It is also a wireway for DLO cables that pass through the lower portion of cabinet to an adjacent meter section. The panel will be de-energized according to MOP. The DLO cables will continue to be energized during the replacement of breaker. The DLO cables do not have to be manipulated in any manner in order to replace the breaker. Does NFPA 70e still consider this working in an electrically energized situation? Please give reference.
 

EC Dan

Senior Member
Location
Florida
Occupation
E&C Manager
The applicable section is 130.2 and defines two conditions for needing to establish an electrically safe work condition for systems above 50 V:

1. Working within limited approach boundary. Only applies to exposed electrical parts, so the pass-through conductors are excluded.
2. Interacting with equipment where conductors or circuit parts are not exposed but an increased likelihood of arc flash hazard exists. Since the conductors pass through the enclosure and are not being manipulated, the risk of arc flash is minimal.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
The applicable section is 130.2 and defines two conditions for needing to establish an electrically safe work condition for systems above 50 V:

1. Working within limited approach boundary. Only applies to exposed electrical parts, so the pass-through conductors are excluded.
2. Interacting with equipment where conductors or circuit parts are not exposed but an increased likelihood of arc flash hazard exists. Since the conductors pass through the enclosure and are not being manipulated, the risk of arc flash is minimal.
what happens if he drops a tool on the DLO conductors while removing the breaker?
 

alexfox1986

Member
Location
Manchester
Occupation
Electrical Engineer
Replacing a breaker in a 480v 3phase panel that is part of a distribution cabinet. It is also a wireway for DLO cables that pass through the lower portion of cabinet to an adjacent meter section. The panel will be de-energized according to MOP. The DLO cables will continue to be energized during the replacement of breaker. The DLO cables do not have to be manipulated in any manner in order to replace the breaker. Does NFPA 70e still consider this working in an electrically energized situation? Please give reference.
Hi! According to NFPA 70E (2021 edition), even if the panel is de-energized, if there are energized conductors or circuit parts in the vicinity of the work being performed, it is still considered electrical work on or near exposed energized conductors or circuit parts, and the appropriate electrical safety practices and personal protective equipment (PPE) must be used.

Specifically, NFPA 70E defines an "energized electrical conductive work" as "work on or directly associated with exposed energized electrical conductors or circuit parts that are not in an electrically safe work condition." An "electrically safe work condition" is defined as "a state in which an electrical conductor or circuit part has been disconnected from energized parts, locked/tagged in accordance with established standards, tested to ensure the absence of voltage, and grounded if determined necessary."

Therefore, in your situation, even though the panel is de-energized, the DLO cables passing through the wireway are still energized, and the work being performed on the panel is considered work on or near exposed energized conductors or circuit parts. You should follow the appropriate electrical safety practices, including wearing the required PPE and following the established lockout/tagout procedures, to protect yourself from potential electrical hazards.

Reference: NFPA 70E (2021), Standard for Electrical Safety in the Workplace, Article 100 Definitions, Article 130 Work Involving Electrical Hazards, and Article 120 Establishing an Electrically Safe Work Condition.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
This a 6 month old thread and the OP has not been back since then. You might want to take notice of the age and interest of threads before wasting time and effort replying. Not trying to be rude just giving some advice.
 

alexfox1986

Member
Location
Manchester
Occupation
Electrical Engineer
This a 6 month old thread and the OP has not been back since then. You might want to take notice of the age and interest of threads before wasting time and effort replying. Not trying to be rude just giving some advice.
Thank you for the advice!
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
This a 6 month old thread and the OP has not been back since then. You might want to take notice of the age and interest of threads before wasting time and effort replying. Not trying to be rude just giving some advice.
I thought the board software was set to close out old threads.
 