Exposed ENT
High Peak
In a 3-story residential property where the first floor is half underground and is used as a basement/garage can ENT be exposed?
362.10 Uses Permitted.
For the purpose of this article, the first floor of a building shall be that floor that has 50 percent or more of the exterior wall surface area level with or above finished grade. One additional level that is the first level and not designed for human habitation and used only for vehicle parking, storage, or similar use shall be permitted. The use of ENT and fittings shall be permitted in the following:
(1) In any building not exceeding three floors above grade as follows:
a. For exposed work, where not prohibited by 362.12
b. Concealed within walls, floors, and ceilings
(2) In any building exceeding three floors above grade, ENT shall be concealed within walls, floors, and ceilings where the walls, floors, and ceilings provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies. The 15-minute-finish-rated thermal barrier shall be permitted to be used for combustible or noncombustible walls, floors, and ceilings.
At three stories or less you are OK without the restrictions of installing the ENT within a required 15 minute building finish for building of more than three stories.