Exposion Proff devices, Water Proof
Not unless they are. There are some XP enclosures that are rated for other environmental conditions. But they are not required to be.
Are explosion proof devices also water-proof, or submersion proof (in water).
Thanks for the help
NEMA
Type 7 Enclosures constructed for indoor use in hazardous (classified) locations classified as Class I, Division 1, Groups A, B, C, or D as defined in NFPA 70.
Type 8 [FONT=Arial,Arial][FONT=Arial,Arial]Enclosures constructed for either indoor or outdoor use in hazardous (classified) locations classified as Class I, Division 1, Groups A, B, C, and D as defined in NFPA 70. [/FONT][/FONT]
Type 6 and 6P is suitable for occasional and prolonged water submersion.
If it is continously submerged in water then you wouldn't need to worry about being explosionproof, would you?:happyno:
[FONT=Arial,Arial][FONT=Arial,Arial][/FONT][/FONT]
[/FONT][/FONT]
Whether something is 'explosion proof' has no connection with whether it is weather proof, oil tight, or submersible. These are separate ratings. There is no "hierarchy' in the NEMA classifications- it's best to consider each as distinct.
Since one of the more common engineering solutions to making something 'explosion proof' is controlled venting, any form of gasketing or sealing could very well defeat the venting.
That said, appliances DO exist that are both submersible and explosion proof. I am thinking, in particular, of some rated sewage pumps. Keep in mind that water can carry with it other fluids, and many of these fluids can separate and become vapor as they move through a pump. Likewise, the pump body can become exposed should the pump run longer than it should.