5 spools at the auction, did win one for about 5 bucks a foot. Tried to buy 2 but last minute bidding went crazy on last 4 spools.
POCO cannot use it per their rules, but it will be AFTER the meter so just NEC and WA state codes.
Probably need a separate enclosure to splice to 3/0 copper to terminate at service panel and meter, but do have some 250 MCM lugs I can add to meter and service panel. Very limited experience with 3/C 250 MCM, but figure 15 inch boxes will work if nothing else to transition to a few feet of 3/0 copper. 800 ft feed gives 6% volt drop at full 200A, but never see that much load anyway and no NEC limit on voltage drop, just the 5% recommendation.