Conversation between a buddy and I, here's the gist:
Suppose an old 2 wire system, no eqc going back to the panel. Original 2 prong recep is broken, needs replaced. According to 406.4(D)2b that non-grounding recep can be replaced with a GFCI type receptacle and marked as No Equipment Ground. (assuming no AFCI protection is required, focusing solely on the grounding aspect)
As this is allowed we assume that code is requiring the GFCI protection in lieu of proper grounding through a separate eqc, thus the receptacle may be used with a certain level of protection provided by the GFCI and this installation is considered "safe".
Here's the meat of the question:
Could you extend that circuit, say cut in a recep 4' above the one described above without adding a ground?
250.130(C)(6) references 406.4(D)2b under branch circuit extensions, not just replacements.
Thoughts?
Suppose an old 2 wire system, no eqc going back to the panel. Original 2 prong recep is broken, needs replaced. According to 406.4(D)2b that non-grounding recep can be replaced with a GFCI type receptacle and marked as No Equipment Ground. (assuming no AFCI protection is required, focusing solely on the grounding aspect)