I have a job coming up where I will have to change the meter can because it has deteriorated. I expect the service lateral conductors to be too short to reach the terminals of the new meter can. Is there a generally accepted method of extending the conductors within the meter can? Can a sealable junction box be installed below the meter can and the lateral conductors be extended from there? If so, can someone ID a suitable j-box?
 
I have a job coming up where I will have to change the meter can because it has deteriorated. I expect the service lateral conductors to be too short to reach the terminals of the new meter can. Is there a generally accepted method of extending the conductors within the meter can? Can a sealable junction box be installed below the meter can and the lateral conductors be extended from there? If so, can someone ID a suitable j-box?



I would drop the meter a few inches, you shouldn't need alot. Don't get a meter with a huge design difference
 
Extending conductors in meter can

Extending conductors in meter can

The present meter can is located about 36 inches off the ground on the top of 2 inch PVC. Conductors are three each 2/0 Aluminum, routed underground from a utility transformer about 70 feet away. The can is already too close to the ground and needs to be raised up if possible.
 
You can splice them. See 230.33.
If they are too short, I'd discuss the situation with POCO. For that short a run arrangements with them might prove less expensive than an enclosure & splicing materials.
 