I am trying to understand the difference between Extension Grade and Thermocouple Grade wire. I can only use Thermocouple grade wire at my sensing point, and I can use extenstion grade wire to extend T/C grade wire. I understand that much.
But when it comes to temperature ratings, I get confused. Ext. grade wire has standard limits of error up to 100 C, whereas T/C grade wire has limits of error that are much higher.
Here is my question: If I need a thermocouple that is to sense up to 200 C, can I use the T/C grade wire in the sensing area (where it is exposed to 200C) and then once outside of the sensing area land in a T/C biased terminal block and then make the rest of the run with Extension Grade wire?
The extension grade wire will not be exposed to temperatures above 100 C, but the signal it is carrying will come from a T/C grade wire that is above 100 C. Is that the correct use of extension grade thermocouple wire?