We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.
If exterior Christmas lights are connected to a GFCI is it safe and law full to use non-weatherproof connectors downstream of the GFCI receptacle (any voltage). Very common observation - what is safe? Comments appreciated.
590.5 Listing of Decorative Lighting.
Decorative lighting used for holiday lighting and similar purposes, in accor-
dance with 590.3(B), shall be listed.
If the lights are listed for exterior use then they will have been tested as a factory assembly for such use. Personally, safety wise, using a properly operating GFCI breaker/receptacle and proper routing of the lights is safe. Running the lights in ways that they can be damaged* (like around handrails) or tripped on, or leaving them out year round, or using damaged/repaired lights would be unsafe imo. Running extension cords in unsafe ways (under doors, under windows) or overloaded to power the lights are also safety concerns.
appears to have standard connections, and is UL listed for outdoor installation. *It also looks like a pretty bad trip hazard installed in the way shown.