Exterior electrical equipment near window

Status
Not open for further replies.

Sparknition

Member
Location
Long Beach Ca.
Occupation
Elecrical Contractor
An inspector made me move a small exterior load center becuase it was within 36" of an operable window.
40 years in the industry and never been called on this. Combed through the NEC and could not find an artical.
Inspector did not site artical number. Emailed and called the head electrical inspector and got no response.
So Cal Edison wants 10" clearance from any window for meter/main service equipment.
This was a 8/16 3R load center feeding an ADU.
Any thoughts? Or did I not find an artical pertaining to this?
THX
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
There is a requirement for clearances to service drops and outsider feeders to openable windows, and the ConEd rule is for services, this is a feeder panel, right?
Your AHJ needs to give you the NEC section.
 
Last edited:

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
An inspector made me move a small exterior load center becuase it was within 36" of an operable window.
40 years in the industry and never been called on this. Combed through the NEC and could not find an artical.
Inspector did not site artical number. Emailed and called the head electrical inspector and got no response.
So Cal Edison wants 10" clearance from any window for meter/main service equipment.
This was a 8/16 3R load center feeding an ADU.
Any thoughts? Or did I not find an artical pertaining to this?
THX
He was wrong, plain and simple.
If the drip loop on an overhead service was within three feet, leave the load center where it is and move the drip loop.
 

Sparknition

Member
Location
Long Beach Ca.
Occupation
Elecrical Contractor
I am in complete agreement with you all. No drip loops or overhead service feeders involed.
Will definitly request artical number in future.
Thx for the responses!
 