NEC 210.70(A)(2)(b) requires an exterior light at all exits from a dwelling unit. However, I can not find anything in the NEC that requires an exterior light outside the doors of commercial occupancies.
The 2003 IBC section 1006.1 says "Illumination required. The means of egress, including the exit discharge, shall be illuminated at all times the building space served by the means of egress is occupied."
To me this says basically every exit has to have an exterior light. Any comments?
In addition IBC 1006.3(5) says " In the event of power supply failure, an emergency electrical system shall automatically illuminate the following areas: The portion of the exterior exit discharge immediately adjacent to exit discharge doorways in buildings required to have two or more exits.
Therefore not only does every exit have to have an exterior light, but that light has to "emergency" if it is one of two or more required exits.
Am I reading this right?
Say I have a retail strip center with 10 bays that have 2-exits, one in the front and one in the back. According to this I need 20 lights, 10 in the front and 10 in the back, on emergency power. Where does it stop? I thought the whole point was to get people out of the building, not light there way home???
The 2003 IBC section 1006.1 says "Illumination required. The means of egress, including the exit discharge, shall be illuminated at all times the building space served by the means of egress is occupied."
To me this says basically every exit has to have an exterior light. Any comments?
In addition IBC 1006.3(5) says " In the event of power supply failure, an emergency electrical system shall automatically illuminate the following areas: The portion of the exterior exit discharge immediately adjacent to exit discharge doorways in buildings required to have two or more exits.
Therefore not only does every exit have to have an exterior light, but that light has to "emergency" if it is one of two or more required exits.
Am I reading this right?
Say I have a retail strip center with 10 bays that have 2-exits, one in the front and one in the back. According to this I need 20 lights, 10 in the front and 10 in the back, on emergency power. Where does it stop? I thought the whole point was to get people out of the building, not light there way home???