exterior gfi off kitchen gfi circuit
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
No you can not. There was a time when the NEC allowed it off the kitchen or bathroom circuit but not any longer.
jwelectric
North Carolina
550.13(E) Pipe Heating Cable(s) Outlet. For the connection of
pipe heating cable(s), a receptacle outlet shall be located on
the underside of the unit as follows:
(1) Within 600 mm (2 ft) of the cold water inlet.
(2) Connected to an interior branch circuit, other than a
small-appliance branch circuit. It shall be permitted to
use a bathroom receptacle circuit for this purpose.
Dennis Alwon
Chapel Hill, NC
Thanks , I did not know this but I doubt that is what an exterior receptacle, the op mentioned, is used for. :grin: I wonder why they allow this?
jwelectric
North Carolina
The reason I pointed this out was because to the number of calls I get about double wide mobile homes that have this type of installation.
The reason this is allowed is because mobile homes are governed by HUD. I am not sure just where they stand today but in the start of the 2002 cycle HUD was mandating the electrical installation in mobile homes by, I believe I am not sure, the 1993 cycle.
hurk27
There up to the 2005 NEC with many changes.
Can be viewed here:
http://ecfr.gpoaccess.gov/cgi/t/tex...v8&view=text&node=24:5.1.4.1.1.9.13.1&idno=24
Little Bill
Tennessee NEC:2017
The circuit is allowed on the inside (bath) because if the GFCI was on the outside and it tripped for some reason, the HO might not know it for a while and the pipes might freeze. If it's on a circuit inside it will most likely be noticed and reset before any freezing of the pipes.