- Location
- Madison WI
- Occupation
- Electrical Designer
Is there anything in NEC 2020 that would prohibit the installation of a 100BASE-T Data cable in the same raceway as power conductors so long as it had the same insulation rating as the power conductors, and is totally outdoors (does not enter a building)? The key here is that it does start from nor enter a building - it's between two pieces of utilization equipment outdoors.
Reference: 300.3 (C) (1) - (paraphrasing) shall be permitted to occupy same equipment wiring enclosure, cable or raceway so long as all conductors have insulation rating equal to minimum circuit voltage.
Reference 90.3 - chpt 8 not subject to 1-7 unless noted
Reference Article 800, part I (General) & II - (Wires and Cables outside and Entering buildings) - nothing noted in part I or part II that would prohibit. Part IV is for within-building installations and does not apply.
Reference: 300.3 (C) (1) - (paraphrasing) shall be permitted to occupy same equipment wiring enclosure, cable or raceway so long as all conductors have insulation rating equal to minimum circuit voltage.
Reference 90.3 - chpt 8 not subject to 1-7 unless noted
Reference Article 800, part I (General) & II - (Wires and Cables outside and Entering buildings) - nothing noted in part I or part II that would prohibit. Part IV is for within-building installations and does not apply.