(exterior) LB and shed door obstruction

Status
Not open for further replies.

Hamberg

Member
Location
SE Pennsylvania - Philly
Occupation
General Contractor
Seem to remember an update that did not allow an access point (LB) that had the possibility to be obstructed!? Wiring a shed and the ideal location for the LB would have one of the double doors obstructing it while open. (re)Looked through all of 110 but I'll be danged if I can find it.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Conduit bodies only need to be accessible which is defined in Article 100 of the NEC. Maybe soneone can post the definition so you can discuss it with your sparky.
 

kwired

Electron manager
Location
NE Nebraska
Conduit bodies only need to be accessible which is defined in Article 100 of the NEC. Maybe soneone can post the definition so you can discuss it with your sparky.
easy, the first definitions listed in art 100:

1657211741569.png

Conduit bodies only need to be accessible, they don't need to be readily accessible.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Even panelboards which have breakers that are required to be readily accessible are often installed in a location where an open door swings in front of the panelboard, requiring the door to be closed to access the panel. The code does not prohibit this type of installation.
 

Hamberg

Member
Location
SE Pennsylvania - Philly
Occupation
General Contractor
Thanks guys!

Not that this makes a difference (in any way shape or form) but my question stemmed from advise from our "go-to" Electrician!? I quoted (2017) ART 100 P1 as well as 110.26 and was told "it was updated..." (should have pressed for a cation :mad:)
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Thanks guys!

Not that this makes a difference (in any way shape or form) but my question stemmed from advise from our "go-to" Electrician!? I quoted (2017) ART 100 P1 as well as 110.26 and was told "it was updated..." (should have pressed for a cation :mad:)
Ah, but you get an A+ for even asking the question. Most GCs are not this detail oriented.
 

Hamberg

Member
Location
SE Pennsylvania - Philly
Occupation
General Contractor
Rough-in conduit inspection this morning. Already mounted the LB on the non-door side, (with this info) I'll ask the township inspector if I'm ok to move to door side. straight run up to the panel from there...
 

Hamberg

Member
Location
SE Pennsylvania - Philly
Occupation
General Contractor
Passed rough-in and the township guy laughed when I told him about our guy saying the box needed to be on the non-door side. Already moved to the better location.

Thanks again for the help!
 