250.32 is not quite the correct code section, but I can see how it could be applied.
A pole is a structure, every structure requires a disconnect, with an exception for luminaire poles. The rule in 250.32 can't be applied to any structures but dwelling units as 225 requires a disconnect for all feeders to a structure, except for dwelling unit outbuildings.
Ground rods at lighting poles are called auxiliary electrodes, no rule requiring them, we often see them installed because: the specs require, the engineer requires, the last job required, or I think its a good idea.