We have typically run a #8 equipment bond to hot tubs. In this situation we ran a 6/3 NMS cable (has a #10 bare ground) to a unit to be installed on a balcony off a residence. I have ordered the #8 and I was plannning on installing it when I read this:
2005 NEC section 680.42 subsection (C):
(C) Interior Wiring to Outdoor Installations In the interior of a one-family dwelling or in the interior of another building or structure associated with a one-family dwelling, any of the wiring methods recognized in Chapter 3 of this Code that contain a copper equipment grounding conductor that is insulated or enclosed within the outer sheath of the wiring method and not smaller than 12 AWG shall be permitted to be used for the connection to motor, heating, and control loads that are part of a self-contained spa or hot tub or a packaged spa or hot tub equipment assembly.
Does this mean I may just use the #10?
[ August 05, 2005, 08:33 PM: Message edited by: grasfulls ]
2005 NEC section 680.42 subsection (C):
(C) Interior Wiring to Outdoor Installations In the interior of a one-family dwelling or in the interior of another building or structure associated with a one-family dwelling, any of the wiring methods recognized in Chapter 3 of this Code that contain a copper equipment grounding conductor that is insulated or enclosed within the outer sheath of the wiring method and not smaller than 12 AWG shall be permitted to be used for the connection to motor, heating, and control loads that are part of a self-contained spa or hot tub or a packaged spa or hot tub equipment assembly.