I have a new 4000A-277/480V switchboard being installed outside of an existing building. The switchboard will re-feed the existing buildings main power panel, but it also feeds panels at two other remote structures and several large pieces of remote equipment. Since the switchboard is not dedicated to or located within the existing building, would the only service grounding requirements for this 4000A switchboard be two ground rods per NEC 250.50 connected with #6 CU per NEC 250.66(A)? Each of the buildings/ structures would be considered remote and need to be provided with individual grounding electrode systems per NEC 50.32.
I'm just looking or me feedback. Did I overlook something here?
Thanks!
I'm just looking or me feedback. Did I overlook something here?