malachi constant
Senior Member
- Location
- Minneapolis
I have an install going in with a 480V exterior pad-mount utility transformer feeding an adjacent connection cabinet. The connection cabinet has no overcurrent protection (which is typical for utility installs in our area). The cabinet will feed some chillers (which have service rated disconnects at them) and also will feed a 480:208V 500kVA step down transformer which in turn feeds the building. There is no disconnecting means in the plans on the primary of the step down transformer - I assume this is illegal and we need to get a primary disconnect ahead of it - that feeding it basically straight from the utility is prohibited.
Then from the stepdown transformer there is an underground run (1600A, not protected) into the building, at which point it immediately hits a 1600A service disconnect. I believe this is legal.
Am I correct that we need a primary on this transformer, and that the service entrance disconnect located within the building is sufficient for the secondary?
Then from the stepdown transformer there is an underground run (1600A, not protected) into the building, at which point it immediately hits a 1600A service disconnect. I believe this is legal.
Am I correct that we need a primary on this transformer, and that the service entrance disconnect located within the building is sufficient for the secondary?