External bus bar to form grounding electrode system and size

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Can an external busbar be used to bond together grounding electrodes to form grounding electrode system? Please see attached. If yes then what size should the external bus bar be? 250.53(C) says binding jumper size to form grounding electrode system should be sized per table 250.66

99e2ef0e94bbb4b27cfbd941e9f39846.jpg
 
250.64(C) says you can use a busbar to interconnect GEC's and 250.64(F)(1) also allows a busbar. The bar in that section says 1/4" thick by 2" wide and the length would be whatever you need to give enough space to terminate al the connections.
 
The width is going to be whatever is wide enough to take the terminations. You have 4 conductors in the drawing. If you put a lug on each and bolt them to the bar side by side, you'd need at least a 4" bar and really I'd like at least a 6".

Table 5A in chapter 9 gives the area of conductors. 4/0 bare copper is .475 sq in.
 