External Conductor in Switchboard section

Status
Not open for further replies.

smarteng

Member
Location
Los Angeles
Hello Everybody,

We have a switchboard 480V, 1600A. One of the sections with un-insulated bus bars of the switchboard has external conductors entering from bottom and existing from the side. Those conductors are also have spliced inside the switchboard section. Conductor feeds circuits which are completely unrelated to the switchboard. Is this acceptable by NEC/Codes and is it safe to have external conductors in a switchboard section with un-insulated bus bars. Please advise.

Thank you.
 

xptpcrewx

Power System Engineer
Location
Las Vegas, Nevada, USA
Occupation
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
Hello Everybody,

We have a switchboard 480V, 1600A. One of the sections with un-insulated bus bars of the switchboard has external conductors entering from bottom and existing from the side. Those conductors are also have spliced inside the switchboard section. Conductor feeds circuits which are completely unrelated to the switchboard. Is this acceptable by NEC/Codes and is it safe to have external conductors in a switchboard section with un-insulated bus bars. Please advise.

Thank you.

I don’t believe it’s prohibited anywhere but you would still need to follow the rules that apply. For example, conductor insulation type, clearances for conductors entering bus enclosures, field identification etc.

Note: Running unrelated circuits through equipment is not the smartest thing. If you have a failure in one circuit you can potentially induce that failure onto the other non related circuit(s). Similarly, to perform work/maintenance on one a piece of equipment would require de-energizing both circuits. Lastly, this can introduce confusion.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Hello Everybody,

We have a switchboard 480V, 1600A. One of the sections with un-insulated bus bars of the switchboard has external conductors entering from bottom and existing from the side. Those conductors are also have spliced inside the switchboard section. Conductor feeds circuits which are completely unrelated to the switchboard. Is this acceptable by NEC/Codes and is it safe to have external conductors in a switchboard section with un-insulated bus bars. Please advise.

Thank you.

See 408.3 A (3).
 
Last edited by a moderator:

smarteng

Member
Location
Los Angeles
I don’t believe it’s prohibited anywhere but you would still need to follow the rules that apply. For example, conductor insulation type, clearances for conductors entering bus enclosures, field identification etc.

Note: Running unrelated circuits through equipment is not the smartest thing. If you have a failure in one circuit you can potentially induce that failure onto the other non related circuit(s). Similarly, to perform work/maintenance on one a piece of equipment would require de-energizing both circuits. Lastly, this can introduce confusion.


Thank you so much.
 