Strathead
- Ocala, Florida, USA
- Electrician/Estimator/Project Manager/Superintendent
I can't get my head around this.... A typical installation in this area is to run separate conductors for grounding electrodes, terminating all of them on a copper ground bar external to the Service Equipment and then running a 250.66 sized conductor to the equipment. To expound, in larger projects running (usually a 3/0) from electric room to electric room terminating on external ground bars utilized to terminate transformer GEC's. The terminations on the ground bars are usually lugs with bolts and nuts. First is this legal? If so, where is the nuance in 250 that allows this? I am thinking we MUST run to a ground bar INSIDE the service equipment for multiple GEC,s. We can then extend to an external ground bus and run to other electrical rooms. Also, confirm for me that 250.30 (5) and (6) that allow us to use the ground bars in separate rooms for separately derived transformers.
Not sure if I was clear with all of my issues. I will know if I see some responses.