External vs internal summed CTs

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
What are the pros and cons of externally summed CTs for low impedance bus bar protection vs a unit that does it internally (like a B90 or SEL487B)?
 

Bugman1400

Senior Member
Location
Charlotte, NC
Back in the day, the pros included a reduction in wire and a reduction in the number of CT inputs to the relay. The cons include failure to diagnose an offending ckt for a through fault and increased saturation (and subsequent higher voltage) for strong buses.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Back in the day, the pros included a reduction in wire and a reduction in the number of CT inputs to the relay. The cons include failure to diagnose an offending ckt for a through fault and increased saturation (and subsequent higher voltage) for strong buses.



Am I correct to assume that current utility practice is to use paralleled CTs only for radial lines? Or can looped transmission lines also be included?
 

Bugman1400

Senior Member
Location
Charlotte, NC
For new construction or an upgrade, I would expect looped (networked) subs to use a dedicated CT input for each line (radial or source). However, I have seen new distribution subs parallel the CTs from two feeder ckts. In that case, I believe the number of feeder ckts exceed the number of CT inputs of the relay.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
For new construction or an upgrade, I would expect looped (networked) subs to use a dedicated CT input for each line (radial or source). However, I have seen new distribution subs parallel the CTs from two feeder ckts. In that case, I believe the number of feeder ckts exceed the number of CT inputs of the relay.

So the way to go then is a B90 or SEL-487B. Just seems easier to parallel them and use a single over current relay instead of 3 bus relays- 6 if the sub has redundant protection. Plus your not limited to 21max inputs.
 