Dsg319
- West Virginia
- Wv Master “lectrician”
I know there’s probably a good reason and I just don’t know it.
Here is the work setting. Natural gas facilities,
Station ground/bonding wire an insulated conductor routed underground bonded to all steel and equipment. Usually have some magnesium anodes in the system too. And havnt dug yet in the drawings to clarify this but most time this station ground is bonded to the GES. But this place is off grid and gets it power from a capstone (which I believe is like a micro turbine. So I’m not sure if the grounding system-is bonded to that power supplys GEC or not. Havnt yet seen if it is delta/wye. For have just been in the roughing in stage conduit,cable tray,etc
But regardless of the fact I’m trying to wrap my head around the use and point of this. We have some motors running some big cooling fans and they call for the grounding/bonding system to also be tied onto the motor itself(externally). Is there something special that it does that a EGC inside the motor doesn’t do?
