I'm working on a pretty small project that is having a few additions to the existing fire alarm system. The reviewer requested that I show the minimum size of the batteries for backup. I ran through the calculations of finding the standby current (0.0549 A) and the alarm current (2.842 A). I'm using a required standby time of 24 hours and a required alarm time of 5 minutes.
Applying a safety factor of 1.2, I am coming up with a required standby capacity of 1.9 Amp Hours. This seems pretty small, so I was wondering what standard size of battery was for your typical small fire alarm system.
(Devices: 1 FACP, 16 Smoke Detectors, 5 Strobes, 4 Horn/Strobe, 3 Pull Stations)
Thanks for the help!
Keri

Applying a safety factor of 1.2, I am coming up with a required standby capacity of 1.9 Amp Hours. This seems pretty small, so I was wondering what standard size of battery was for your typical small fire alarm system.
(Devices: 1 FACP, 16 Smoke Detectors, 5 Strobes, 4 Horn/Strobe, 3 Pull Stations)
Thanks for the help!