NFPA 72 Section 12.3 Pathway Class Designations.
12.3.7 Class X. A pathway shall be designated as Class X when it performs as follows:
(1) It includes a redundant path.
(2) Operational capability continues past a single open, and the single open fault results in the annunciation of a trouble signal.
(3) Operational capability on metallic conductors continues past a single short-circuit, and the single short-circuit fault results in the annunciation of a trouble signal.
(4) Operational capability on metallic conductors continues past a combination open fault and ground fault.
(5) Conditions that affect the intended operation of the path are annunciated as a trouble signal.
(6) Operational capability on metallic conductors is maintained during the application of a single ground fault.
(7) A single ground condition on metallic conductors results in the annunciation of a trouble signal.