Jim1959
Senior Member
- Location
- Longmont, CO
I have a customer who is requesting that we fabricate breaker panels for one of our gas chromatograph buildings utilizing CID2 DIN rail mount breakers inside a couple of Hoffman CSD enclosures. It will be in an area operated by an industrial group. There will be one general purpose panel with about 10 breakers. There will be another UPS fed panel that will have about 4 breakers. There will be a 3rd 480 volt feeder to the building heater. My understanding is that I need to install 3 disconnects ahead of the panels and heater, to keep it under six operations of the hand - 225.33 A. My concern is that they would need to open the enclosures in order to operate the breakers, with exposed energized parts. They would have to do so with respect to 70E, but is this a compliant installation to start with? It will save them money over classic NEMA 7 breaker panels. I do see breakers inside control cabinets often, so it is probably OK. Thoughts?