Need your Help Here!
I have a 18-60R receptacle used in a hotel for events (4 pole - 4 wire). The receptacle is wired according to it NEMA configuration - 3 phase - 60A - 120/208V (three Hots and a Neutral, no ground). The hotel electrician has made a tempoary panel with Edison outlets for customers to use on a tempory event basis. The 18-60P plug (4 pole) and cord (5 wire) wired to this temporary panel has the ground conductor pulled out of the cord and is attached to a lug on the metal face plate of the 18-60R receptacle. I'm sure its not code compliant, but what NEC articles apply here?
I have a 18-60R receptacle used in a hotel for events (4 pole - 4 wire). The receptacle is wired according to it NEMA configuration - 3 phase - 60A - 120/208V (three Hots and a Neutral, no ground). The hotel electrician has made a tempoary panel with Edison outlets for customers to use on a tempory event basis. The 18-60P plug (4 pole) and cord (5 wire) wired to this temporary panel has the ground conductor pulled out of the cord and is attached to a lug on the metal face plate of the 18-60R receptacle. I'm sure its not code compliant, but what NEC articles apply here?