Are there any code requirements for duct work installed into an electrical enclosure for facility AC cooling (vs. a dedicated air conditioner)?
One possible issue I see is temperature control.
If the chiller is controlled by thermostat(s) in the facility, could you have problems with the cabinet overheating for example on a cool day when the AC requirements for the facility are minimal? Or in the winter when the building is heated and the AC is not even running.
No NEC issue afaik.
It's done in data centers all the time. The raised flooring is used as the supply air plenum and enclosed racks are cooled by air pressure up through them. In other areas they just put in perforated floor panels where you want air. That system works well and has been widely used for they past 50 years. Another bad idea I have seen done in a few television facilities is a plenum over a group of racks forcing cold air down. This does not work very wells at all since most equipment pulls cool air in the front and discharges hot air from the back or sides. You end up with excessive back pressure on the equipment cooling fans and poor heat removal.
There are also cabinet coolers that use compressed air. And Hoffman has small ac units for control panels, and they may be able to maintain the NEMA panel rating.
This is all good, but the first sentence in post #2 answered the OP’s question.
but you know how much we all love to answer unasked questions.