• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

FACP Battery wiring in same junction box as NAC

Status
Not open for further replies.

highriser

Member
Location
San Francisco
Occupation
Tech
Can wiring from FACP to an external battery (24V 40Ah) in its own conduit be run through the same 4x4 junction box as wiring from FACP to power supplies and power supplies to notification appliances?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Can wiring from FACP to an external battery (24V 40Ah) in its own conduit be run through the same 4x4 junction box as wiring from FACP to power supplies and power supplies to notification appliances?
Is the cable from the FACP to the power supplies the FACP on-board NAC circuit going out to trip the remote booster power supplies? If "yes", then the answer is probably, "no". The cable going from the battery box to the FACP is considered non-power limited, while the NAC's are power limited and they should not be mixed in the field.
 