Hi,
First i would like to say that I like this site where we can share information:).
I have small issue, there is a new Fire Alarm Control Panel-FACP recieved recently. it's 220 volts line to nuetral. our system is 380volts/220volts. the problem is the breaker used for this FACP is single pole 20 amperes the wire size is 12 AWG:confused:. what do you think guys?

Thank you:).
 

Dennis Alwon

Moderator
Staff member
If the voltage is 220 line to neutral then a single pole breaker is all you need--unless I am missing something.
 

DARUSA

Senior Member
How many amp is the unit?
As long the breakers is rated for 220 volts I see no problem.
#12 is rated for 20amps
 