Hi All,
For a panel with only EV chargers load (which are LCL per NEC), does the load per phase (A, B, C) have to time 1.25?
Of course the feeder conductor size is 125% of the continuous load per 215.2(A) but I guess the VA consumed by the chargers is a fixed number even the car is charged more than 3 hours.
In other words, the feeder is sized per 215.2(A) but the total connected load of 90A (before multiply by 1.25) is acceptable for a 100A panel in my opinion.
Any inputs would be appreciated.
For a panel with only EV chargers load (which are LCL per NEC), does the load per phase (A, B, C) have to time 1.25?
Of course the feeder conductor size is 125% of the continuous load per 215.2(A) but I guess the VA consumed by the chargers is a fixed number even the car is charged more than 3 hours.
In other words, the feeder is sized per 215.2(A) but the total connected load of 90A (before multiply by 1.25) is acceptable for a 100A panel in my opinion.
Any inputs would be appreciated.