Inside a 3 phase 45 kva dry type typical 480v-208/120 step down transformer (the one I examined) there was a factory installed bonding strap from the enclosure threaded stud to the core support structure. Is there an internal factory connection from that support structure to the XO terminal?
I ask this because I had to investigate why a FACP and a few FAPS (all the same fire alarm manufacturer and everything existsing for decade+) several feet from this transformer all a had a alternating normal and power loss trouble when all readings were proper for 30 minutes when I was there. But inside the transformer although the GEC conductor ( to building steel) was connected to XO with panel neutral, the panel's EG conductor was going to the xfmr's enclosure stud. The panel's neutral and ground bar were separated. All conductors were in flexible metal conduit. I think there should be an additional bonding conductor between the neutral lug and the enclosure stud but I don't know if the xfmr already has it. I don't think it does.
I ask this because I had to investigate why a FACP and a few FAPS (all the same fire alarm manufacturer and everything existsing for decade+) several feet from this transformer all a had a alternating normal and power loss trouble when all readings were proper for 30 minutes when I was there. But inside the transformer although the GEC conductor ( to building steel) was connected to XO with panel neutral, the panel's EG conductor was going to the xfmr's enclosure stud. The panel's neutral and ground bar were separated. All conductors were in flexible metal conduit. I think there should be an additional bonding conductor between the neutral lug and the enclosure stud but I don't know if the xfmr already has it. I don't think it does.