I have a question regarding factory installed "Handy boxes" used for "Mushroom" type exhaust fans mounted on roof.
Table 314.16(A)
(3 x 2 x 1 1/2) Device box can contain 3 12 AWG conductors.
The exhaust fan is feed by a 12/2 MC with 12/2 SO cable for the load side. The device yoke counts as 2 conductors per 314.16 (B)(4). That is seven conductors, four conductors over. The device box is full before the Device or Branch circuit conductors is installed.
How can the factory installation be sufficient?
The code states that Factory installations are Code compliant.
Any feedback would be appreciated. Thank you for your time and effort. Happy New Year and GOD Bless.