inspector 102

Senior Member
Location
Northern Indiana
A contractor has cut the factory molded plug off of a lighting transformer, run the SJ cord down a stud cavity and wired it directly to switch to control accent lighting in a bedroom. I have indicated that this is a violation of the NEC and needs to be corrected. He says prove it. Can anyone help me with all the specific code references I can show him. This contractor has always been a bit difficult to work with and I would just like to prove my point with all the code sections that I can. Thank you.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: Factory molded plugs

You didn't say if the transformer had been UL listed or labeled. But if it was, you might cite 110.3(B).
 
A

a.wayne3@verizon.net

Guest
Re: Factory molded plugs

Originally posted by renosteinke:
Code forbids the use of temporary cord (SO,SJ, etc.) in place of permanent wiring.
The original thread said that it was a cord connected transformer how would that be temporary wiring?????????????/
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Factory molded plugs

Allen, the original thread also said the plug was cut off and the "SO" was wired directly in to a switch. This would make the "SO" pretty much permanent wouldn't you think? So with the uses allowed and not allowed the "SO" would be in violation in this instance.

Roger

[ April 11, 2003, 07:10 PM: Message edited by: roger ]
 