Customer had an existing 200A service mounted on a pole with a meter; customer brought in a mobile home and set it 75' away. The existing service fed a barn, and has its own ground rod already.
We ran a 4-wire feeder from the existing service to a 200A disconnect on a pedestal next to the mobile home, and continued to the home. Two ground rods were installed at the pedestal for compliance with 250.32(A).
I was not there for the inspection yesterday, but they required us to remove the ground rods from the disconnect, saying this was a violation and created two different grounding potentials.
Guys am I missing something?
Sent from my iPhone using Tapatalk
We ran a 4-wire feeder from the existing service to a 200A disconnect on a pedestal next to the mobile home, and continued to the home. Two ground rods were installed at the pedestal for compliance with 250.32(A).
I was not there for the inspection yesterday, but they required us to remove the ground rods from the disconnect, saying this was a violation and created two different grounding potentials.
Guys am I missing something?